估计是没钱了 想榨点钱 一会说要装smoke alarm 要2w 我说不装 不是必须的
过几天又说什么
Wormald recently carried out routine testing and inspection of your fire and safety systems at ################. During the testing and inspection our technicians highlighted the following faults/defects that require further investigation and/or repair: 1. Circuits 1, 3, 4, 5, 6, and 7 failed their insulation mega test. All tests are below 5 mega Ohms. As per NZS4512 1981 section 202.2 they require to be above 5 meg-Ohms. Cabling requires to be replaced. We recommend you undertake the repairs to ensure this system remains compliant with the appropriate NZ Standard and does not affect your Building Warrant of Fitness in the near future. This letter is a notification.
意思是要重新扑线???我可以自己找电工做吗
|